Main Circuit Breaker - Replacement - AD0286
Service Home How To Procedures Main Circuit Breaker - Replacement - AD0286
17.1 Main Circuit Breaker - Replacement
Recently Updated Last updated: 02/08/2021
AD0286
This procedure tells you how to replace the main circuit breaker in the electrical cabinet. The circuit breaker in the kit can be different from the installed circuit breaker, but it operates the same.
Kit Required: CIRCUIT BREAKER REPLACEMENT KIT
Breaker Amperage 15A 20A 40A 80A 125A
Kit P/N 93-2550 93-2551 93-2552 93-2553 93-2554
Push [POWER OFF].
 Danger: Disconnect the electrical service to the machine.
 Important: With and AC Volt meter, measure across the L1 - L3 on top of the main breaker. If AC voltage is still present go to the source and check that the correct service breaker was disconnected.
 Danger: After you disconnect the service to the machine, wait for the LEDs on the early power-fault detection module (EPFDM) and the vector drive to go off fully. This may take 20 or more minutes.
Record the color sequence of the main electrical supply wires [1] that go to the circuit breaker [2]. Disconnect the wires.
Disconnect the contactor cables [3] from the circuit breaker.
If the contactor [5] is installed on the rear of the circuit breaker, disconnect the (3) transformer cables [4] at the transformer.
Remove the circuit breaker assembly [2] from the machine.
Remove the circuit breaker from the breaker mount bracket.
Discard the circuit breaker if it is not under warranty.
Use (2) long screws [4] to attach the new circuit breaker [2] to the breaker mount bracket [1].
Select the holes on the bracket that allow the switch on the circuit breaker to fit through the hole on the locking bracket [5].
Use (3) short screws [3] to attach the locking bracket [5] to the breaker mount bracket [1].
Select the holes on the locking bracket that allow the toggle [6] to move freely.
 Note: The circuit breaker you receive may look different from the one illustrated. Assembly is the same.
Do this step only if the contactor was installed on the rear of the used circuit breaker assembly.
  • Install the the contactor adapter bracket P/N 25-12101 [2] to the back wall of the cabinet.
  • Install the contactor [3] included in the kit to the adapter bracket.
  • Connect the cables going to the contactor.
The bracket for the circuit breaker assembly has (2) sets of holes to attach it to the electrical cabinet.
Look at the circuit breaker.
  • If the circuit breaker is the same as a breaker in the first group [1], use the top set of holes.
  • If the circuit breaker is the same as a breaker in the second group [2], use the bottom set of holes.
Attach the circuit breaker assembly to the electrical cabinet.
Install the main breaker cover. Refer to Main Breaker Cover Installation procedure included in the kit.
Connect the cables. Refer to Haas Main CIrcuit Breaker - Torque Specifications for what value to torque the circuit breaker power leads.
Turn on the electrical service to the machine, and test for correct operation and phasing.