CAN Bus Systems - Troubleshooting Guide - TG0043
Service Home CAN Bus Systems - Troubleshooting Guide - TG0043
- Jump to Cause - Back to Top
9.1 CAN Bus Systems Troubleshooting Guide
Recently Updated Last updated: 10/10/2025
TG0043
Revision C - 05/2026
Controller Area Network (CAN) is a robust vehicle bus standard designed to allow microcontrollers and devices to communicate with each other. This method is used to create satellite nodes grouped by function that can be expanded on without changing the core electronics.
Each board has a node ID selection switch [SW2] that must be set correctly.
Devices are connected in Daisy Chain.
Each board has a termination switch [SW1] that must be set correctly.
Note: The last device on the chain needs to be terminated.
The overall CAN System sequence should be connected in the order that follows: Active Ballscrew Compensation > CAN E-Vise > Compact APL > Motion Sensor > CAN Autodoor.
Important: The CAN system at the end of the sequence will vary by machine and depends on what options the machine has. The last CAN system in the sequence should have their termination switch on the TERM setting. The only exception of this is if the Motion Sensor is the last CAN System in the sequence, this board does not have a termination switch and will need a jumper (PN: 32-1306) installed at J3 if it is the last CAN System.
Board Locations
1.  VMC CAN Spindle Head PCB
2. CAN Lube Panel PCB
Updated
3.  UMC CAN Spindle Head PCB
Note: For UMC-400 machines, the spindle head CAN box IO is located at the back of the ram, not at the top of the spindle head.
4. Lathe CAN Spindle Head PCB
5. CAN Autodoor
6. CAN E-Vise
Node ID Selection
Device Node ID Factory Setting
IO Board 3 N/A
CAN Autodoor 13 (D on selector) 9013.001
CAN Electric Vise 11 (B on selector) 9011.001
CAN Lube Panel 5 9005.001
CAN Spindle Head 7 9007.001
Legacy CAN Autodoor 9 9009.001
Compact APL 15 (F on the selector) 9015.001
Active Ballscrew Compensation 20 (4 on the selector) 9020.001
Updated
 IMPORTANT: If the I/O board loses communication with a CAN system, it will stop communicating with all other devices on the CAN network.
IMPORTANT: Resolve the CAN communication fault completely before proceeding with further troubleshooting.
ALARM / CAN CODE
BEFORE SOFTWARE 100.21.000.1100:
Alarm 9898.001: CAN NODE WARNING
CAN code [0x43]: CAN NODE WARNING
SOFTWARE 100.21.000.1100 and Later:
Alarm 9706 or (100.001): CAN NODE COMMANDED CURRENT OUT OF RANGE
CAN code [0x43]
Outdated Firmware & Parameters Upgrade to the latest Software, Configuration files, and I/O / CAN AD Firmware.
Alarm 9701: Node ID: XX Node reported it lost communication from I/O board
CAN code [0x01]
Old IO firmware. Load I/O firmware 4.09 or greater.
Poor connection Verify CAN Bus Connectors are fully seated and termination resistor set correctly.
Alarm 9899 IOPCB CAN FAULT and/ or Alarm 9105 IO BOARD COMMAND EXECUTION FAILURE The CAN node I/O Configuration is incorrect. Update the I/O configuration via the I/O Config tab.
The incorrect CAN node is enabled. Verify that Factory Settings 9000.001 -> 9031.001 are set correctly. Only active nodes should be enabled.
The Autodoor CAN PCB does not have power. Verify that the Low Volt Power supply is supplying power to the CAN Autodoor PCB.
The CAN node Communication cable is disconnected. Power down machine for at least a minute. Verify all CAN communication cables are connected correctly.
The CAN Module ID Selector is incorrect. Power down machine for at least a minute. Set ID selector correctly. Power up machine.
The CAN Modules have incorrect termination. Power down machine for at least a minute. Verify that only last node in the chain is terminated. Power up machine.
The CAN Node needs to be reset. Disable CAN Node via 9000.001 -> 9031.001. If the machine recovers (I/O page isn’t “X”) after disabling a particular node, try to enable the node again.
Alarm 9798: IOPCB CAN FCT CRC MISMATCH A test of the internal CRC for the Factory Config Table (FCT) located on one of the CAN devices does not match the CRC for the machines FCT. This can happen due to power failure at a critical time or after replacement of a CAN board attached to the I/O board
  1. Press [POWER OFF].
  2. Put the USB memory device into the control.
    Note: The USB memory device must contain your Haas Control Key and the correct configuration files.
  3. Press [POWER ON].
  4. Press [DIAGNOSTIC].
  5. Go to I/O Config in the Diagnostics tab.
  6. Press [F3] to Update Config Table.
  7. Press [RESET] to continue. If the alarm does not clear, cycle the machine power.
The Main CRC and the Factory CRC are now the same.
CAN code [0x43]: Invalid clamp value
Alarm 9706: Invalid clamp value
CAN code [0x43]
Outdated autodoor/Evise firmware Update the autodoor/evise to 1.06 or newer
CAN code [0x44]: Invalid voltage command
Alarm 9707: Invalid voltage command
CAN code [0x44]
Alarm 9899.001: CAN BUS OFF ERROR
Alarm 9700: CAN BUS OFF ERROR
Poor connection Verify CAN Bus Connetors are fully seated and termination resistor set correctly.
Short circuit on CAN Bus
Use multimeter to diagnose short circuit:
  1. Power down machine
  2. Disconnect all nodes
  3. Reconnect nodes one at a time while measuring resistance between CAN lines and 12V and Ground on the connectors
  4. Replace the node that results in a short circuit
Note: It should be 60 ohm between CAN-H and CAN-L
9899.002: CAN BUS OFF ERROR
CAN code [0x01]: Node reported it lost communication from I/O board
Alarm 9701: Node reported it lost communication from I/O board
CAN code [0x01]
CAN code [0x30]: I/O board reported it lost communication from node
Alarm 9702: I/O board reported it lost communication from node
CAN code [0x30]
I/O mapping missing node Verify in I/O Config tab that the node is mapped. Get the latest configuration from portal.
Incorrect node enabled Verify that Factory settings 9000.001 - 9031.001 are only set to true for the nodes that are installed in the machine.
Node ID set incorrectly on node Select correct node ID on ID selection switch. Reboot the machine.
Node lost power Use a multimeter to verify that the node has power. Replace the power supply if necessary.
Poor connection Verify that the CAN Bus Connectors are fully seated and that the termination resistor set correctly.
Alarm 9899.003: CAN BUS OFF ERROR
Alarm 9703: CAN NODE ERROR
Node Fatal alarm. Firmware has a non-recoverable alarm. Cycle node enable (90nn.001) or update config table in I/O page. The machine may need to be rebooted.
Alarm 9713: NODE APPLICATION CORRUPTED I/O Board has detected a CAN device with corrupted application&nbsp;firmware. Try updating the firmware for the affected CAN device.
Alarm 9714: NODE BOOTLOADER CORRUPTED I/O Board has detected a CAN device with corrupted bootloader firmware.
ALARM 966 EXCESSIVE TOOL IMBALANCE (board accelerometer) Excessive tool vibration is generated by on board accelerometer Verify that everything is properly balanced, such as tools and spindles
Reduce sensitivity using Setting 245
  • Setting 245 = Normal: Means that parameter 856 is directly used
  • Setting 245 = Low: Means that parameter 856 is multiplied by 1.5
  • Setting 245 = Off: Alarm 966 will not be thrown.
NOTE: Setting 245 will not persist when the power is cycled
Please refer to the  Accelerometer Troubleshooting Guide for further information
ALARM 9941 CRASH DETECTED (spindle head accelerometer)  The machine detected a crash Verify the program machine movements to make sure the machine does not crash
The Accelerometer unit, cable or spindle head CAN board is damaged
  • Verify analog inputs are not 0 (cable unplugged)
  • I/O board minimum version 4.09 (update to latest if possible)
  • Spindle head CAN board minimum 1.10 (update to latest if possible
  • Make sure to take an error report (SHIFT+F3), error reports will have information about the crash direction and magnitude in the JavaConsoleLog.txt file (refer to Crash Detection Section in the Accelerometer Troubleshooting Guide for further information)
Electrical Diagrams
CAN Bus sequence when a machine has Active Ballscrew Compensation, CAN E-Vise, Compact APL, Motion Sensor, and CAN Autodoor.
CAN Bus sequence when a machine has a CAN E-Vise, Compact APL, and CAN Autodoor.
The CAN Lube Panel and CAN Spindle Head PCB diagram with a CAN Autodoor and a CAN E-Vise
The CAN Lube Panel and CAN Spindle Head PCB diagram with a CAN Autodoor and without a CAN E-Vise
The CAN Lube Panel and CAN Spindle Head PCB diagram with a CAN E-Vise, but without a CAN Autodoor
The CAN Lube Panel and CAN Spindle Head PCB diagram without a CAN Autodoor or CAN E-Vise
Related Content
Smart CAN Autodoor TSG
CAN Lube Panel and Spindle Head TSG
DIagnostic Data
Firmware Update
I/O Troubleshooting