26 - NGC - Robot and Automation
Next Gen Control Electrical - Service Manual
  • 1 - NGC - Introduction
  • 2 - NGC - Activation
  • 3 - NGC - Software Update
  • 4 - NGC - Firmware Update
  • 5 - NGC - Configuration
  • 6 - NGC - Error Report and Backup
  • 7 - NGC - Main Processor
  • 8 - NGC - I/O and TC PCB
  • 9 - NGC - CAN Systems and Autodoor
  • 10 - NGC - Servo Motors and Axis Cables
  • 11 - NGC - 4th and 5th Axis
  • 12 - NGC - Servo Amplifiers
  • 13 - NGC - Vector Drive
  • 14 - NGC - Regen
  • 15 - NGC - 320V Power Supply
  • 16 - NGC - Wye / Delta
  • 17 - NGC - Circuit Breaker and Transformer
  • 18 - NGC - PSUP PCB
  • 19 - NGC - SKBIF and LCD Monitor
  • 20 - NGC - Remote Jog Handle
  • 21 - NGC - 115V LED - WorkLights
  • 22 - NGC - CabCool
  • 23 - NGC - MyHaas
  • 24 - NGC - Networking
  • 25 - NGC - 8M PCB
  • 26 - NGC - Robot and Automation
  • 27 - NGC - Machine Data Collection
  • 28 - NGC - Control Icons
  • 29 - NGC - Sensors and Switches
  • 30 - NGC - USB
  • 31 - NGC - Keypad
  • 32 - NGC - Broken Tool Detection
  • 33 - NGC - IPFDM PCB
  • 34. NGC - LVPS
  • 36 - NGC - High Intensity Lights
  • 26.1 Haas Robot Package
  • 26.2 Non Haas Robot Integration
  • 26.3 Haas APL
  • 26.4 Haas Bar Feeder
  • 26.5 Pallet Pool
26.1 - Haas Robot Package
Haas Robot Package - Service Manual
Click on the image below to take you to the Haas Robot Package - Service Manual
Robot Integration Aid - NGC
RD0057
This document is intended to aid in the integration of a robot on a machine with the Next Generation Control (NGC). Haas Service and Applications personnel can help to make sure that the CNC machine operates correctly. Haas personnel are not responsible for robot configuration or robot cell setup. Always consult with robot integrators to help with your robot application.
 Danger: Some service procedures can be dangerous or life-threatening. DO NOT attempt a procedure that you do not fully understand. If you have any doubts about doing a procedure contact your Haas Factory Outlet (HFO) and schedule a service visit.
Machine Requirements
  • The machine must have NGC software version 100.16.000.1030 or higher.
  • P/N: 93-MFININ This is the internal M-Fin function cable.
  • P/N: CNC This is a 15' external M-Fin function cable. For a 30' cable order P/N: CNC30.
  • P/N: 93-1157 8M option. This kit adds 8 additional M-codes user relays to the NGC control.
    Note: If the machine is equipped with a non-servo autodoor option it will already have the 8M PCB option installed. A Mill with a non-servo autodoor uses 4 out of the 8 available user relays for operation. A Lathe with a non-servo autodoor uses 2 out of the 8 available user relays for operation. If more user relays are needed a secondary 8M PCB can be installed, refer to 8M Option - Installation.
  • P/N: 93-2889 User relays and Terminal Plug connector kit.  Order this kit if your machine has I/O PCB P/N 34-3490B installed.
  • Probe option
  • Autodoor option, or a device to open the door.
Robot Cell
Robot Location:
  • Select an area for the robot cell.
  • Make a drawing of the equipment positions on the floor. A 3 ft (1 m) space on all sides of each CNC machine is recommended for usual maintenance access.
This illustration shows a typical robot cell. The CNC machines are located in a half-circle configuration with the robot in the center.
 Note: Robots are made to turn 0 - 360 degrees. Robots cannot turn through the zero (0 degrees) mark. Think about this when you design the robot cell. Put the zero (0 degrees) position in an area that the robot does not travel to.
  • A - CNC Machine A
  • B - CNC Machine B
  • C - CNC Machine C
  • D - Robot
  • E - Completed Parts
  • F - Un-finished Parts
  • G - Optional Station 1
  • H - Optional Station 2
 Capacity
  • Be sure to select a robot with sufficient capacity for the size and weight of the un-finished part.
Chip Removal
  • Many machines have a conveyor or auger that puts chips in a receptacle. If the receptacle is inside of the robot cell, you must have a procedure to remove these chips.
Gaurding:
  • You must install a permanent structure to keep personnel out of the robot cell. This structure is very important.
  • You must install physical and electronic locks on the structure entrance.
 Note:  Give access to the keys for the physical locks only to authorized personnel. The electronic lock must send a signal to stop the robot when the structure door opens.
  • The robot arm has a standard mounting point for a gripper.
  • The grippers are usually made to hold a specific un-finished part. Make sure that the gripper can move the un-finished part as it changes through the machining process.
Material Movement and Optional Stations
  • Include areas where the robot can pick up un-finished parts and put completed parts. Some applications require a place to put a partially completed part, possibly to change its position or to wait for a CNC machine. Typically, this is a strong stand.
  • Make sure that the stands do not interfere with the robot’s movement as it works in other areas of the cell.
Tool Life
  • Think about the length of time a tool is used when you operate a robot cell.
  • Time must be scheduled to examine and replace tools. Use the Haas Advanced Tool Management to increase the time between tool maintenance. This function allows for backup tools. This function is standard on Haas mills and lathes.
Workholding: Mills:
  • The customer must supply the workholding fixture and sensors.
 Note: Pneumatic fixtures are recommended for pressures below 150 psi (10.3 bar).
Workholding: Lathes
  • The customer must supply the workholding sensors.
  • Chuck sensors can be installed in the coolant collector. The "clamped" sensor must activate when the chuck is fully closed. The "unclamped" sensor must activate when the chuck is fully open. When the chuck holds an un-finished part, neither sensor will be active.
Robot Integration Example
This illustration shows a Robot installed on the right side of a VMC.
  • The robot loads the raw material through the right side window.
  • The side window is being open/closed by an air cylinder [1] . The robot control the operation of the air cylinder .
  • There is an open and close proximity sensors mounted on the side window.  The robot monitors the condition of the window sensors.
  • There is a pneumatic vise [3] mounted on the table. The machine controls the operation of the vise.
Note: This robot setup does not have a cell safe signal as the side window status is not being monitored by the Haas control.
  1. Window Open / Close, Air Cylinder
  2. Robot Arm
  3. Pneumatic vise
  4. Side Window
  5. Robot Cage
  6. Haas VMC
This G-code program shows the handshaking sequence between the Haas Control and the Robot.
  • CNC: Preparatory G-Code
  • CNC: Move table to the load position
  • CNC: Open the vise and wait for the vise to fully open
  • CNC: Call the robot. (M23 Load blank sequence)
  • Robot: Open the window, and wait for window to be fully open.
  • Robot: Arm loads the raw material into the vise. Sends M-Fin Signal to CNC.
  • CNC: Close the vise and wait for the vise to fully close.
  • CNC: Call the Robot. (M24 Retract from machine)
  • Robot: Arm retracts from the machine.
  • Robot: Closes the window. Sends M-Fin Signal to CNC.
  • CNC: Probes X and Y location.
  • CNC: Runs the 1st operation.
  • CNC: First operation is done. Call the Robot. (M25 Flip part sequence)
  • Robot: Grabs the part. Sends M-Fin Signal to CNC.
  • CNC: Call the Robot. (M21 Flip the part)
  • Robot: Arm Flips the part. Sends M-Fin Signal to CNC.
  • CNC: Call the Robot. (M24 Retract from machine).
  • CNC: Runs the 2nd operation.
  • CNC: Done with 2nd operation. Move the table to the load position
  • CNC: Call the Robot. (M22 Remove Finish Part Sequence)
  • CNC: Call the Robot. (M23 Retract from machine)
  • Robot: Arm retracts part from the machine. Sends M-Fin Signal to CNC.
  • CNC: Program end, repeat program.
Note: The wiring diagrams shown below were used for the Robot integration example listed above and may not work with your application.
  • Emergency Stop Circuit
  • Clamp / Unclamp Solenoid
  • M-Fin Signal Relay
  • 8M PCB wiring
  • Air Cylinder Solenoid
  • Gripper Solenoid
  • Window Sensors
Robot E-stop Connection
[E-Stop] Signal: CNC to Robot
There is two methods for sending an [E-stop] signal from the machine to the robot safety circuit.
Method 1:  (recommended)
Use TB1-B terminals 9 and 10 to wire in a auxiliary relay to signal the robot safety circuit (see illustration).  The Haas CNC will switch the relay ON/OFF  when any of the [E-stop] buttons are activated or deactivated.  The relay output NO, NC contacts can then be connected to the Robot safety circuit.
  • External voltage is required to drive the relay coil.
  • External voltage range 0V to 60VDC is allowed.
  • The load should not draw more than 30mA.
Note:  Haas recommends using this method as it involves minimum integration with the machine.
Method 2:  (Legacy)
Install extra NC or NO contactor to the back of each [E-stop] button in the machine.  Then wire the contactors in a daisy chain and feed the signal to the robot.  When the [E-stop] button is pressed the signal from the contactors will be sent to the robot safety circuit.
You can order these contactors from your local Haas distributor.
  • P/N 61-0046A Normally open contactor.
  • P/N 61-0047A Normally closed contactor.
Note:  There is no remote [E-Stop] reset signal available.  Once the machine is in a [E-stop] state, the only way to reset is to physically pull the [E-stop] button and then press the [Reset] button twice.
[E-stop] Signal: Robot to CNC
Use TB1-B terminals 7, 8, 11 and 12 to connect the robot [E-stop].
Remove JP1 from the I/O PCB.
  • Connect [E-STOP] NC contact to TB-1B terminals 7 and 8.
  • Connect [E-STOP] NO contact to TB-1B terminals 11 and 12.
To view the status of the Robot to CNC [E-Stop] inputs:
  1. Press the DIAGNOSTIC button and go to the I/O tab.
  2. Type keyword "STOP" and press the F1 button.
  3. Find inputs 70 ESTOP MASTER and 98 RR_REDUNDANT_ESTOP.
  4. Press the switch and make sure the input bits toggle from 0 to 1 and vice versa.
     Note: The control will display E-STOP (4) icon when the auxiliary E-stop button is pressed.
Cell Safe Methods
The Cell Safe feature allows a program to continue running while the door is open in order to accommodate the use of the machine within a robot cell. Robot integrators are responsible for ensuring a safe cell enclosure. The presence of a robot cell is verified by detection of a signal which is sent from the robot cell to the control in one of two methods. Either or both can be used.
Note:  On a VMC only the front doors are being monitored by the control, the side windows status are not being monitored.  The side windows have a mechanical lock  that can be locked with a key.
Method 1: Cell Safe Input Pulse
The robot sends a pulse signal to the CNC control.
  • The machine monitors the cell safe input for the discrete pulse.
  • This pulse can be created by triggering a relay with a square wave (3-10 hertz @ 50% duty cycle).
  • The (NO or NC) contacts of the relay can then be connected to I/O PCB TB1-A at terminals 3 & 6.
    Note: Damage to the I/O PCB will occur if external voltage is applied to these input terminals.
To view the status of cell safe input pulse:
  1. Press the DIAGNOSTIC button.
  2. Go into the I/O tab.
  3. Type in CELL.
  4. Press the F1 button.
When the pulse if being received by the control the input #103 CELL_SAFE value will toggle from 0 to 1.
Method 2: Macro Variable Timer
For the second method the robot writes a value in program macro variable #3196 by Ethernet.
This variable can be read at any time but it can only be set by Ethernet, not a g-code program. It has a range of 0-5000 milliseconds. The timer will count down from this value. When it reaches zero, the cell is no longer considered safe. In order to maintain continuity of cell safe, this variable should be reset before its counter reaches zero.
Note: The second method may be better for use with a deadman switch, or in the robot’s teach mode.
For more information on how to write to machine variables refer to Machine Data Collection - NGC.
The machine monitors both signal methods for the presence of a cell safe signal when there is a program running. This feature does not need to be enabled or disabled. If a door is opened when a cell safe signal is present, the active program will continue while the door is open. When there is a valid cell safe signal and the door is open, the spindle speed is limited. The maximum spindle speed is the value of Setting 292, Door Open Spindle Speed Limit. If the door is opened while the spindle speed is above this speed, the spindle will decelerate to the speed limit.
If a door is opened and the cell is NOT safe, the machine will go into a door hold—axis motion stops and the spindle speed is limited.
M-Codes Relays
The NGC I/O PCB has (5) user relay outputs. The 8M option has (8) user relay outputs.
These relays can be operated in two methods.
Method 1: On / Off
The M59 Pnnn (ON) and M69 Pnnn (OFF) codes can be used to activate probes, auxiliary pumps, clamping devices, etc. Connect these devices to the terminal strip for the individual relay. These relay contacts are isolated from all of the other circuits and can switch up to 120 V ac at 3.0 A. The relays are Single Pole Double Throw (SPDT).
Note: Pressing the RESET button turns off any activated M-code relay.
Method 2: Turn on and Wait for M-Fin Signal
The  M29 Pnnn (Mills) and M129 Pnnn (Lathes) codes are use to call a robot to perform a task.  When the Haas control executes these codes it will turn on a relay and wait for the robot to complete the task.  The robot will complete the task and then send a M-FIN signal to the Haas control.  When the Haas control receives the M-Fin signal it will turn off the relay and continue with the program.
Note: Pressing the RESET button stops any operation waiting for a relay-activated accessory to finish.
User M-Codes Relay Functions Codes Table
This table has the address codes for the 5 User relays on the I/O PCB and three 8M option PCB's installed. As of software version 100.19.000.1400 the M-code relay reset behavior has changed. If more M-codes are needed refer to 8M Installation procedure.
  • User Relay Location - This column gives the physical location of each relay either on the I/O PCB or 8M option PCB
  • Turn On - This column lists the M codes that trigger the relay on.
  • Turn Off - This column lists the M codes that trigger the relay off.
  • Turn On and Wait for M-Fin Signal - This column lists a different set of M codes that trigger the relay on while waiting for a finish signal that triggers the relay off.
  • Will Turn Off with [RESET], [E-STOP] or ALARM - This column lists how each configuration reacts differently to [RESET], [E-STOP] or an ALARM.
I/O PCB
User Relay Location Turn On Turn Off Turn On and Wait for M-FIN Signal Will Turn Off with [RESET], [E-STOP] or Alarm
I/O PCB M21 TB3A: 1,2,3 M59 P114 M69 P114 Mills: M29 P114, Lathes: M129 P114 YES
I/O PCB M22 TB3A: 4,5,6 M59 P115 M69 P115 Mills: M29 P115 , Lathes: M129 P115 YES
I/O PCB M23 TB3B: 7,8,9 N/A - Haas Robot Pkg Only¹ N/A - Haas Robot Pkg Only¹ N/A - Haas Robot Pkg Only¹ YES
I/O PCB M24 TB3B: 10,11,12 N/A - Haas Robot Pkg Only¹ N/A - Haas Robot Pkg Only¹ N/A - Haas Robot Pkg Only¹ YES
I/O PCB M25 TB2: 1,2,3 M59 P112 M69 P112 Mills: M29 P112 , Lathes: M129 P112 YES
NOTE:
  1. User relays M23 and M24 on the I/O PCB are configured from the factory to be used by the Haas Robot Package.  If you do not have the robot option the function of these two relays can use by the user only if the User Relay Kit is purchased.  Refer to User Relay Service Update.
Bank #1
8M PCB #1 (JP1 and JP5) M21 M59 P90 M69 P90 Mills: M29 P90 , Lathes: M129 P90 YES¹
8M PCB #1 (JP1 and JP5) M22 M59 P91 M69 P91 Mills: M29 P91 , Lathes: M129 P91 YES¹
8M PCB #1 (JP1 and JP5) M23
M59 P92 M69 P92 Mills: M29 P92 , Lathes: M129 P92 YES¹
8M PCB #1 (JP1 and JP5) M24
M59 P93 M69 P93 Mills: M29 P93 , Lathes: M129 P93 YES¹
8M PCB #1 (JP1 and JP5) M25
M59 P94 M69 P94 Mills: M29 P94 , Lathes: M129 P94 YES¹
8M PCB #1 (JP1 and JP5) M26
M59 P95 M69 P95 Mills: M29 P95 , Lathes: M129 P95 YES¹
8M PCB #1 (JP1 and JP5) M27
M59 P96 M69 P96 Mills: M29 P96 , Lathes: M129 P96 YES¹
8M PCB #1 (JP1 and JP5) M28
M59 P97 M69 P97 Mills: M29 P97 , Lathes: M129 P97 YES¹
NOTE:
  1. Behavior of bank 1 (JP1) changes when the “Status Relays” feature is enabled. (Factory Setting 315.26).  For more information on this feature refer to MDC - 8M OPTION STATUS RELAYS.
Bank #2
8M PCB #2 (JP2 and JP5) M21¹
M59 P103 M69 P103 Mills: M29 P103 , Lathes: M129 P103 YES/NO²
8M PCB #2 (JP2 and JP5) M22¹
M59 P104 M69 P104 Mills: M29 P104 , Lathes: M129 P104 YES/NO²
8M PCB #2 (JP2 and JP5) M23¹
M59 P105 M69 P105 Mills: M29 P105 , Lathes: M129 P105 YES/NO²
8M PCB #2 (JP2 and JP5) M24¹
M59 P106 M69 P106 Mills: M29 P106 , Lathes: M129 P106 YES/NO²
8M PCB #2 (JP2 and JP5) M25¹
M59 P107 M69 P107 Mills: M29 P107 , Lathes: M129 P107 YES/NO²
8M PCB #2 (JP2 and JP5) M26¹
M59 P108 M69 P108 Mills: M29 P108 , Lathes: M129 P108 YES/NO²
8M PCB #2 (JP2 and JP5) M27¹
M59 P109 M69 P109 Mills: M29 P109 , Lathes: M129 P109 YES/NO²
8M PCB #2 (JP2 and JP5) M28¹
M59 P110 M69 P110 Mills: M29 P110 , Lathes: M129 P110 YES/NO²
 NOTE:
  1. For machines built after 2019 without a pallet changer, only outputs P106 through P109 on Bank #2 work. If more outputs are needed, switch Bank #2 to Bank #3 in order to use outputs P79 through P86, but make note that Bank #3 relays do not turn off with [RESET], [E-STOP], or an alarm. Another way to gain spare outputs is to install service kit 93-3913 2ND 8M SPARE NGC ADDON that replaces Bank #2 (spare outputs are restricted on machines with C-APL), refer to the 8M Option - Installation - AD0162 procedure for more information.
  2. Some factory options, such as Autodoor and APL, use relays from Bank #2 and Bank #4 when enabled. If these options are installed on your machine, the used relays may or may not turn off upon reset.
Bank #3
8M PCB #3 (JP3 and JP5) M21 M59 P79 M69 P79 Mills: M29 P79 , Lathes: M129 P79 NO
8M PCB #3 (JP3 and JP5) M22 M59 P80 M69 P80 Mills: M29 P80 , Lathes: M129 P80 NO
8M PCB #3 (JP3 and JP5) M23 M59 P81 M69 P81 Mills: M29 P81 , Lathes: M129 P81 NO
8M PCB #3 (JP3 and JP5) M24 M59 P82 M69 P82 Mills: M29 P82 , Lathes: M129 P82 NO
8M PCB #3 (JP3 and JP5) M25 M59 P83 M69 P83 Mills: M29 P83 , Lathes: M129 P83 NO
8M PCB #3 (JP3 and JP5) M26 M59 P84 M69 P84 Mills: M29 P84 , Lathes: M129 P84 NO
8M PCB #3 (JP3 and JP5) M27 M59 P85 M69 P85 Mills: M29 P85 , Lathes: M129 P85 NO
8M PCB #3 (JP3 and JP5) M28 M59 P86 M69 P86 Mills: M29 P86, Lathes: M129 P86 NO
M-Fin Signal
The M-Fin function can be setup by installing the internal wire harness P/N: 93-MFININ , and using the M-Fin cable P/N:CNC to interface with the robot.
M-Fin Input: The M-Fin signal input is necessary when using the M29 Pxxxx M-codes. The pins 3, 4 are used for this input.
Important: Use a relay to activate this input (see illustration). Do not apply voltage to this input. When a M-Fin signal is sensed the diagnostic #18 M_FIN_INPUT bit will toggle.
M-Fin Output: This is a normally open relay built into the I/O PCB. The pins 1,2 are used for this relay. This relay can be activated with a M59 P4 or deactivated with a M69 P4.
Robot Door Sensors
On Haas machines, it is recommended that the control pendant and door open sensors are installed. These sensors will provide an input to the robot that can be used to determine if it is safe to operate. Any proximity sensor can be used for these applications. The control pendant proximity sensor is used to confirm that the pendant is in a safe position for robot operation. The door open sensors confirm the autodoors are completely open and it is safe to enter the machine.
If your machine has 2 doors, such as in a VMC, you can install 2 sensors, one for each door, and then have to separate inputs or wire them in series as shown below so that both must be energized to send a signal.
External sensors can either be directly wired to the robot, or can be wired to an interface used for communication with the robot.
Setting 276 - Fixture Clamp Input Number
This setting specifies the input number to monitor for workholding fixture clamping.
The machine will generate alarm 180 FIXTURE NOT CLAMPED:
  • If you command the spindle to start while the fixture clamp input indicates that the workholding is not clamped.
  • if the fixture clamp input signal changes while the spindle is turning.
Note: This feature only monitors the sensor during Feed motion. It will not monitor the sensor during a rapid motion or handle jog.
The illustration shows an auxiliary pressure switch integration. The ground is connected to Terminal 6. Terminal 5 is input #97 WORK_HOLD_CLAMP. For this example, Setting 276 is set to 97.
Note: The Work Hold Clamp Input should be trigger by a NC or NO air sensor.  No voltage should be connected to this input,  because there is already a 12v power supply, the sensor will act as a switch to trigger the input.
User Inputs
User Inputs on the I/O PCB
The I/O PCB includes a set of (2) available inputs (100 (#11100) and 101 (#11101)) at TB5.
Note: Devices connected to these inputs must have their own power supply.
When a device applies 10-25 VDC between Pins 1 and 2, the input 100 bit (Macro #11100) changes from 1 to 0.
When a device applies 10-25 VDC between pins 3 and 4, the input 101 (Macro #11101) bit changes from 1 to 0.
References
  • Machine Data Collection - NGC
  • 8M Option - Installation
26.3 Haas APL Service Manual
Haas APL - Service Manual
Click on the image below to take you to the Service Manual
26.4 Haas Bar Feeder - Service Manual
26.5 Pallet Pool - Service Manual