Active Ballscrew Compensation - Troubleshooting Guide
Service Home Active Ballscrew Compensation - Troubleshooting Guide
Recently Updated Last updated: 05/29/2024
- Jump to Cause - Back to Top
9.5 Active Ballscrew Compensation Troubleshooting Guide
Controller Area Network (CAN) is a robust vehicle bus standard designed to allow microcontrollers and devices to communicate with each other. This method is used to create satellite nodes grouped by function that can be expanded on without changing the core electronics.
Each board has a node ID selection switch [SW2] that must be set correctly.
Devices are connected in Daisy Chain.
Each board has a termination switch [SW1] that much be set correctly.
Note: The last device on the chain needs to be terminated.
Overview
The Active Ballscrew Compensation is made up of:
  1. Linear Gauge Sensor - The sensor assembly is installed at the end of the ballscrew.
  2. CAN Node Box - CAN node box that feeds the information from the sensor to the CAN hub board.
  3. Linear Gauge Hub Board -CAN board the sends feedback info from the sensor to the IO board.
Each Axis will have its own Linear Gauge Sensor [1] and CAN Node Box [2] that will connect to the CAN Hub Board [3].
The cables coming from each of the axis' CAN Node Box will connect to the following ports on the CAN Hub Board:
  • X-Axis: Sensor 1 Port
  • Y-Axis: Sensor 2 Port
  • Z-Axis: Sensor 3 Port
At this time Active Ballscrew Compensation is an option on the following machines and their variants:
  • VF-6/7/8/9/10/11/12/14
  • VR-8/9/11/14
  • VM-6
Node ID Selection
Device Node ID Factory Setting
IO Board 3 N/A
CAN Autodoor 13 (D on selector) 9013.001
CAN Electric Vise 11 (B on selector) 9011.001
CAN Lube Panel 5 9005.001
CAN Spindle Head 7 9007.001
Legacy CAN Autodoor 9 9009.001
Compact APL 15 (F on the selector) 9015.001
Active Ballscrew Compensation 20 (4 on the selector) 9020.001
Alarm / CAN code
Possible Cause Corrective Action
Cannot upgrade the CAN board firmware. The I/O board has a firmware version earlier than 4.24. Upgrade the I/O firmware to 4.24 or higher. Try upgrading the CAN board firmware after the I/O firmware is upgraded.
Alarm 9417: LINEAR SENSOR FAULT DETECTED Invalid reading from linear sensor has been detected. The sensor may be disconnected. Verify all hardware connections are secure and correct Refer to the Overview section above for all the components in the system, the wiring diagram can be found below for where it lies within the CAN system.
Alarm 9105: IO BOARD COMMAND EXECUTION FAILURE
The machine outputs the following alarms with this alarm:
  • 2001.003: EMERGENCY STOP SWITCH ERROR
  • 2002: OPERATOR'S PENDANT EMERGENCY STOP SWITCH ERROR
  • 120: LOW AIR PRESSURE OR FLOW
Outdated main I/O firmware.
Updated the main I/O firmware to the latest version.
Refer to the Firmware Update procedure.
Alarm 9899: IOPCB CAN FAULT and/ or 9105: IO BOARD COMMAND EXECUTION FAILURE The CAN node I/O Configuration is incorrect. Update the I/O configuration via the I/O Config tab.
The incorrect CAN node is enabled. Verify that Factory Settings 9000.001 -> 9031.001 are set correctly. Only active nodes should be enabled.
The CAN node Communication cable is disconnected. Power down the machine for at least a minute. Verify all CAN communication cables are connected correctly.
The CAN Module ID Selector is incorrect. Power down the machine for at least a minute. Set ID selector correctly. Power up machine.
The CAN Modules have incorrect termination. Power down the machine for at least a minute. Verify that only the last node in the chain is terminated. Power up machine.
The CAN Node needs to be reset. Disable CAN Node via 9000.001 -> 9031.001. If the machine recovers (I/O page is not “X”) after disabling a particular node, try to enable the node again.
Alarm 9798: IOPCB CAN FCT CRC MISMATCH A test of the internal CRC for the Factory Config Table (FCT) located on one of the CAN devices does not match the CRC for the machines FCT. This can happen due to power failure at a critical time or after replacement of a CAN board attached to the I/O board
  1. Press [POWER OFF].
  2. Put the USB memory device into the control.
    Note: The USB memory device must contain your Haas Control Key and the correct configuration files.
  3. Press [POWER ON].
  4. Press [DIAGNOSTIC].
  5. Go to I/O Config in the Diagnostics tab.
  6. Press [F3] to Update Config Table.
  7. Press [RESET] to continue. If the alarm does not clear, cycle the machine power.
The Main CRC and the Factory CRC are now the same.
Alarm 9701: CAN NODE LOST COMMUNICATION WITH IO
CAN code [0x01]
Old IO firmware. Load I/O firmware 4.09 or greater.
Poor connection  Verify CAN Bus Connectors are fully seated, and termination resistor set correctly.
Alarm 9702: IO LOST COMMUNICATION WITH CAN NODE
CAN code [0x30]
I/O mapping missing node Verify in I/O Config tab that the node is mapped. Get the latest configuration from portal.
Incorrect node enabled Verify that Factory settings 9000.001 - 9031.001 are only set to true for the nodes that are installed in the machine.
Node ID set incorrectly on node Select correct node ID on ID selection switch. Reboot the machine.
Poor connection Verify that the CAN Bus Connectors are fully seated, and that the termination resistor set correctly.
Alarm 9703:
CAN NODE ERROR
Node Fatal alarm. Firmware has a non-recoverable alarm. Cycle node enable (90nn.001) or update config table in I/O page. The machine may need to be rebooted.
Alarm 9737.00X: Linear Sensor Error
Sub-codes:
.001 = X-Axis
.002 = Y-Axis
.003 = Z-Axis
The sensor node has lost communication with the linear sensor. This may be due to a faulty sensor or loose connection to the Node.
1. Verify the cable connection of the linear sensor to the node.
2. Under the diagnostics tab, navigate to the I/O page, and check the analog input for the axis generating the alarm.
  • A-Input 27 = X-axis
  • A-Input 28 = Y-axis
  • A-Input 31 = Z-axis
3. If possible, apply pressure to the switch by hand to see if the analog value increases as the switch is pushed in. Verify the input is not constantly 0.
4. Also verify that the input is not fluctuating when a constant/no pressure is applied to the switch.
Wiring Diagram
CAN Bus sequence when a machine has a Ballscrew Linear Sensor, CAN E-Vise, Compact APL, and CAN Autodoor.
CAN Bus sequence when a machine has Active Ballscrew Compensation, CAN E-Vise, Compact APL, Motion Sensor, and CAN Autodoor.